Old   October 8, 2011, 09:20
Default Room air conditioning (pressure increase problem)
  #1
New Member
 
Join Date: Mar 2011
Posts: 5
Rep Power: 15
unas is on a distinguished road
Hi, I'm trying to simulate heat transfer from house to envoirment and find heat losses through walls, door, window etc..I'm using FloEFD. There is an air conditioner which has inlet volume flow rate with high temperatrure(30oC). I've also added outlet volume flow with same rate. I got 2 issues;

1) When I run the analyze, pressure inside the house drastically increases (to nonsense values). If I increase the outlet flow rate like 2 times higher, pressure inside the house drastically decreases. Then I changed the outlet flow with environment pressure and the issue solved but I'm not sure about the environment pressure has no effect on heat losses. What else can i do to fix this problem?

2) I've also added some radiators and add volume sources(with heat generation rate) to them. Heat conduction in solids active, problem is external(to take into account the effects of wind), time dependent but the sources have no effect on temperature distrubution. I've checked toggle for the source..

Thank you

Last edited by unas; October 8, 2011 at 09:23. Reason: grammar
unas is offline   Reply With Quote

Old   October 17, 2011, 07:05
Default
  #2
Disabled
 
Join Date: Jul 2009
Posts: 616
Rep Power: 23
Boris_M will become famous soon enough
Hi unas,

1.
It is the correct way to define an outlet pressure condition. The pressure condition does work exactly as the real life condition. The heat loss is only by the fluid leaving through the opening with the calculated temperature. This is the way to set it up.
The calculation always takes into account to have a balanced mass. That means what enters the simulation has to leave again, but only in terms of mass. If you define a volume flow rate for 30°C inlet and another one as outlet with the same amount of volume flow then you don't consider the same mass as the temperature at the outlet can be different and with a given volume flow rate the mass is different than at the inlet, thus haveing the mass balance not fulfilled and you suck either more or less mass out of your building causing a lower or higher pressure because of the different density of air for the inlet and outlet temperature according to the equation:
Mass=Volume*desnity
And we all know the desity of air is lower for hotter temperatures.
With a pressure opening you satisfy the needs for a mass balance and giving the system a "releasing valve" as the pressure can be released and is not forced to build up by the limitation on how much has to flow out.
You could also define inlet and outlet mass flow rate but the recommended way is to use an outlet pressure condition.

2.
The heat sources should have an effect. But do you need time dependency? Because this process can take quite long in real life already. The best way to test it is using really high heat source so you get a very high internal temperature and a very low external temperature and neglect the wind in this test. For example having 500°C inside and -100°C outside and you should see the temperature gradient through the wall and then the same for 60°C inside and 0°C outside. All in steady state for the test.
Do you want to see how long it takes to cool down or heat up or why are you unsing transient? The steady state should show you that it works and if you need transient it takes longer (not always suitable for a quick test) and make sure to manually specify the manual time step in the calculation control options as you would otherwise calculate very tiny steps per interation and therfore probably don't see much changes over a long calculation time. Usually you get time steps automatically around miliseconds or smaller and with such processes taking up to hours it would cause an extreme calculation time.

I hope this helps,
Boris
Boris_M is offline   Reply With Quote

Old   April 11, 2012, 22:52
Default
  #3
New Member
 
lihui
Join Date: Jun 2010
Posts: 12
Rep Power: 15
lihui54312 is on a distinguished road
Quote:
Originally Posted by Boris_M View Post
Hi unas,

1.
It is the correct way to define an outlet pressure condition. The pressure condition does work exactly as the real life condition. The heat loss is only by the fluid leaving through the opening with the calculated temperature. This is the way to set it up.
The calculation always takes into account to have a balanced mass. That means what enters the simulation has to leave again, but only in terms of mass. If you define a volume flow rate for 30°C inlet and another one as outlet with the same amount of volume flow then you don't consider the same mass as the temperature at the outlet can be different and with a given volume flow rate the mass is different than at the inlet, thus haveing the mass balance not fulfilled and you suck either more or less mass out of your building causing a lower or higher pressure because of the different density of air for the inlet and outlet temperature according to the equation:
Mass=Volume*desnity
And we all know the desity of air is lower for hotter temperatures.
With a pressure opening you satisfy the needs for a mass balance and giving the system a "releasing valve" as the pressure can be released and is not forced to build up by the limitation on how much has to flow out.
You could also define inlet and outlet mass flow rate but the recommended way is to use an outlet pressure condition.

2.
The heat sources should have an effect. But do you need time dependency? Because this process can take quite long in real life already. The best way to test it is using really high heat source so you get a very high internal temperature and a very low external temperature and neglect the wind in this test. For example having 500°C inside and -100°C outside and you should see the temperature gradient through the wall and then the same for 60°C inside and 0°C outside. All in steady state for the test.
Do you want to see how long it takes to cool down or heat up or why are you unsing transient? The steady state should show you that it works and if you need transient it takes longer (not always suitable for a quick test) and make sure to manually specify the manual time step in the calculation control options as you would otherwise calculate very tiny steps per interation and therfore probably don't see much changes over a long calculation time. Usually you get time steps automatically around miliseconds or smaller and with such processes taking up to hours it would cause an extreme calculation time.

I hope this helps,
Boris
yes,absolutly correct.
Li hui
lihui54312 is offline   Reply With Quote

Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
mass flow in is not equal to mass flow out saii CFX 12 March 19, 2018 05:21
Sealed room air flow dave_k FLUENT 0 March 15, 2010 03:46
seeking for help about a room with negative pressure mengyue1 FLUENT 0 November 26, 2009 06:40
Does star cd takes reference pressure? monica Siemens 1 April 19, 2007 11:26
Hydrostatic pressure in 2-phase flow modeling (long) DS & HB Main CFD Forum 0 January 8, 2000 15:00


All times are GMT -4. The time now is 20:22.