Default FloVENT and PCR method question
  #1
Senior Member
 
Martin Hegedus
Join Date: Feb 2011
Posts: 500
Rep Power: 19
Martin Hegedus is on a distinguished road
Sorry, I'm from the compressible CFD world and this may seem like an ignorant question to incompressible folks.

Anyway, I was checking out the data sheet for FloVENT and the solver section says "The conjugate nature of heat transfer is concurrently solved using a preconditioned conjugate residual solver together with a flexible cycle multi-grid solution technique."

Not really sure what that is. Is this a time accurate solver? FloVENT is used for HVAC of rooms so I assume it is. But, in my compressible world, a multi-grid solution method is not time accurate.

Also, what equations are begin solved and how are they coupled? I assume that the conservation of mass is incompressible. So is the energy equation coupled to the momentum with the equation of state or is the density in the momentum equation also incompressible (i.e. constant), thus uncoupling the energy equation? However, uncoupling the energy equation seems opposite of what "conjugate nature of heat transfer" means. Also, if the energy equation is uncoupled, I assume buoyancy is not modeled. Which seems odd. Is buoyancy modeled?
Martin Hegedus is offline   Reply With Quote

Old   March 2, 2012, 08:58
Default
  #2
New Member
 
Robin Bornoff
Join Date: Mar 2009
Posts: 23
Rep Power: 17
RobinB is on a distinguished road
Density can either assumed to be constant (valid for low mach no. and, for HVAC, when you don't have the massive density variations you might encounter with fire modelling) or derived using the the ideal gas law ((molecular weigth x (p+ref p))/(RxTabs)). One thing FloVENT doesn't do is shock capture which, for HVAC, I think is OK.

Buoyancy is modelled either using the Boussinesq assumption when density is assumed to be constant (gravitational force per unit volume = g x expansivity x density x (T - Tref)) or if density is set to be variable gravitational force per unit volume = g x (density - reference density).

Multi grid solver is used to accelerate the solution of the temperature variable, that's all.

Going back to your question, the conservation of mass therefore need not assume constant density and thus can be considered compressible.

We normally say that if you get dTs in the model > 60degC leading to about >20% change in volumetric expansion then use the ideal gas law.

You can turn off buoyancy and thus decouple the hydrodynamic and temp equations but should be done with caution, only when forced convection dominates. If in doubt do two models, one with grav on, the other off, if they differ, use grav on.

If you want any more feel free to contact me at robin_bornoff@mentor.com. I'm the FloVENT product manager by the way.
Martin Hegedus likes this.
RobinB is offline   Reply With Quote

Old   March 2, 2012, 11:03
Default
  #3
Senior Member
 
Martin Hegedus
Join Date: Feb 2011
Posts: 500
Rep Power: 19
Martin Hegedus is on a distinguished road
Hi Robin, thank you for your response. In regards to both the content and posting it here at cfd-online. If I have any questions about FloVENT I'll email you directly. But, unfortunately and at this point, it will probably have to wait for the next project.
Martin Hegedus is offline   Reply With Quote

Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 16:41.