Old   January 30, 2025, 06:21
Default Heat rate through cooling jacket result inquiry
  #1
Member
 
Johan M
Join Date: May 2021
Posts: 39
Rep Power: 6
Johan M is on a distinguished road
Hi Everyone,
I am doing a simplified scenario of simulating a helical cooling jacket that will wrap around a motor. The fluid is water. The inlet of the jacket is 20C and the outlet is expected to be 30C.The motor will release a heat load of 1900W.
This simulation did not model the conduction of the walls surrounding the jacket. Instead, I worked out the heat flux produced by the motor from the heat transfer rate of 1900W and the motor exterior surface area. I applied this heat flux to the inner faces of the cooling jacket in the thermal section of the boundary condition tab as a heat flux condition. I had a pressure inlet with a fixed thermal pressure, and a mass flow outlet.
My simulation results displayed a 6C increase in outlet temperature and and negative heat rate of -1800W. The heat transfer rate through my inner walls were +800W and suspiciously the inlet was +1000W. The net heat transfer rate was more or less 0W
I can’t seem to understand:
1. Why there is a heat transfer rate across the inlet?
2. Why the heat transfer rate through the inner wall is not 1800W?
My reference values for enthalpy were 0.
Additionally, I ran an area weighted average of the wall flux with the Total surface heat flux variable on the inner wall and got the heat flux I specified at the start of the simulation. The inlet is at 20C as specified.
Any advice would be appreciated
Attached Images
File Type: png 1.png (129.7 KB, 4 views)
File Type: png 2 Cross section of cooling jacket.png (52.7 KB, 5 views)
Johan M is offline   Reply With Quote

Old   February 4, 2025, 02:12
Default
  #2
Senior Member
 
Moritz Kuhn
Join Date: Apr 2010
Location: Germany, Dresden
Posts: 236
Rep Power: 18
MKuhn is on a distinguished road
The energy balance deals with enthalpy differences. So the difference the heat flux of inlet and outlet should be your heat from the motor. The net heat transfer rate should be 0 (so all right here, maybe you can add a screenshot), if not, you have to run the simulation some more iterations, even if the energy residuals are already converged. What is the mass flow?
MKuhn is offline   Reply With Quote

Old   February 12, 2025, 06:31
Default
  #3
Member
 
Johan M
Join Date: May 2021
Posts: 39
Rep Power: 6
Johan M is on a distinguished road
Quote:
Originally Posted by MKuhn View Post
The energy balance deals with enthalpy differences. So the difference the heat flux of inlet and outlet should be your heat from the motor. The net heat transfer rate should be 0 (so all right here, maybe you can add a screenshot), if not, you have to run the simulation some more iterations, even if the energy residuals are already converged. What is the mass flow?

Thanks Mkuhn,

The mass flow rate differences were very low. Other temperature monitors were flat lined. I didn't realize that the temperature at the inlet brings a heat transfer rate of its own into the system

Kind regards,
Johan
Johan M is offline   Reply With Quote

Old   February 12, 2025, 07:53
Default
  #4
Senior Member
 
Moritz Kuhn
Join Date: Apr 2010
Location: Germany, Dresden
Posts: 236
Rep Power: 18
MKuhn is on a distinguished road
Quote:
Originally Posted by Johan M View Post
Thanks Mkuhn,

I didn't realize that the temperature at the inlet brings a heat transfer rate of its own into the system

And the outlet brings the same heat transfer out of the system plus your motor heat.
MKuhn is offline   Reply With Quote

Reply

Tags
heat flux., heat transfer boundary, heat transfer cooling

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help needed: Simple pipeline flow heat exchange, yet the total heat transfer rate re RC_Jiang FLUENT 0 March 25, 2024 20:49
Total heat transf. rate vs Total surface heat flux Renato Sousa FLUENT 1 April 14, 2020 03:27
No-error UDF for wall heat generation rate but no heat is exchanged?!? NPs Fluent UDF and Scheme Programming 0 May 11, 2017 06:19
Heat Generation rate in W/m³ ashghan OpenFOAM Programming & Development 0 June 27, 2014 05:42
How can I increase Heat Transfer at Domain Interf? B.Simon CFX 3 October 28, 2008 18:53


All times are GMT -4. The time now is 17:57.