Setting Fan Static Pressure
Hi all,
I want to set fan static pressure in Phoenics VR but there is only air velocity or flowrate for user to input. Can anyone here advise me ? The scenario I am facing is the pressure display from inlet to outlet via fan is negative despite having the correct airflow directional arrow display. Can anyone here know what is wrong ? Great thanks. Regards Low |
Hi Low,
To set a fixed pressure the object type you want is an OUTLET, although this is named outlet you can still have inflow here, so it is more accurately a fixed pressure boundary. I think this will help you set the fan static pressure. As for the airflow direction I would check that you have the pressure outlet set correctly relative to the ambient and reference pressure. Thanks, Harry |